A 500 MW, 3-phase, Y-connected synchronous generator has a rated voltage of 21.5 kV at 0.85 p.f. The line current when operating at full load rated conditions will be

Options:
A)

13.43 kA.

B)

15.79 kA.

C)

23.25 kA.

D)

27.36 kA.

Solution:

Ans:(c)